Determine the ampacity for nine 3/0 AWG THHN aluminum conductors in a three-inch RMC at 35°C with only six current-carrying conductors.

Prepare for the Electrical Code Calculations Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Ensure your success on the exam!

To determine the ampacity for nine 3/0 AWG THHN aluminum conductors in a three-inch rigid metal conduit (RMC) at 35°C with only six current-carrying conductors, it is important to refer to the ampacity values provided in the National Electrical Code (NEC) and to apply any necessary derating factors.

For 3/0 AWG aluminum conductors, the base ampacity at an ambient temperature of 30°C (86°F) is typically around 100 amperes per NEC Table 310.16. However, when there are multiple conductors in a conduit, the ampacity must be derated to prevent overheating due to insufficient cooling.

In the case of having six current-carrying conductors, the NEC requires a derating factor. According to the NEC, for more than three conductors, the ampacity must be reduced based on the number of conductors. When you have six current-carrying conductors, a derating factor of 80% applies.

Calculating the derated ampacity involves multiplying the base ampacity by the derating factor:

  • Base ampacity for 3/0 aluminum = 100 A.

  • Derating factor for six