What is the ampacity of three 8 AWG THWN copper conductors installed in EMT at an ambient temperature of 40°C?

Prepare for the Electrical Code Calculations Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Ensure your success on the exam!

To determine the ampacity of three 8 AWG THWN copper conductors installed in EMT (Electrical Metallic Tubing) at an ambient temperature of 40°C, it is important to refer to the National Electrical Code (NEC) tables, particularly Table 310.16 for conductor ampacity.

For 8 AWG copper conductors, under normal conditions at a temperature of 30°C, the base ampacity is typically around 50 amps. However, since the ambient temperature is higher at 40°C, adjustments need to be made according to NEC guidelines.

The NEC provides an adjustment factor for temperature increases. At 40°C, the appropriate adjustment factor is generally 0.82 for conductors rated at 90°C. Thus, calculating the adjusted ampacity involves multiplying the base amperage by this adjustment factor:

  • Base Ampacity for 8 AWG THWN at 30°C = 50 A

  • Adjustment Factor for 40°C = 0.82

Calculating the adjusted ampacity:

50 A x 0.82 = 41 A

This rounded down leads to a more realistic assessment of the maximum amount of current the conductors can safely carry at a higher temperature. The nearest ampacity value