What is the ampacity of three 8 AWG THWN copper conductors installed in EMT at an ambient temperature of 30°C if they are all current-carrying conductors?

Prepare for the Electrical Code Calculations Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Ensure your success on the exam!

To determine the ampacity of three 8 AWG THWN copper conductors installed in Electrical Metallic Tubing (EMT) at an ambient temperature of 30°C, it is essential to refer to the National Electrical Code (NEC) guidelines which provide the necessary ampacity values for various conductors and installation conditions.

For 8 AWG THWN conductors, the base ampacity at 30°C is typically around 55 A, based on NEC Table 310.16. However, since the question specifies that all three conductors are current-carrying, we must apply the appropriate adjustment factors due to the presence of multiple conductors.

According to NEC Article 310.15, when more than three conductors are installed together in a conduit, an adjustment factor is required for the ampacity. For three current-carrying conductors, the adjustment factor is typically 70%. Thus, the calculation is as follows:

  1. Start with the base ampacity for a single 8 AWG THWN copper conductor, which is 55 A at 30°C.

  2. Apply the adjustment factor: 55 A x 0.7 = 38.5 A.

However, this does not match the answer provided

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy